Can I model a tank which has three different inputs and outputs?

Hello, I´m modelling a system in energyplus that has three cooling towers and three chillers and all of them are coupled to one accummulation tank. What object can I use? (I tried to use ThermalStorage:ChilledWater: Mixed but I just can put one inlet and one outlet node). The inlets of the accumulation tank comes from the cooling towers and then goes to the chiller.

I also want to know which object can I use for a stratified tank that can have also three inlets. Thank you

mayks's avatar
61
mayks
asked 2020-02-19 05:59:59 -0500
__AmirRoth__'s avatar
4.4k
__AmirRoth__
updated 2020-03-08 11:41:42 -0500
edit flag offensive 0 remove flag close merge delete

Comments

add a comment see more comments

2 Answers

1

I can suggest an idea...

Your Cooling Towers would be on the supply side of a plant loop, on parallel branches. Then it mixes via the PlantLoop Mixer, goes to the demand side, at which point you just place a WaterHeater:Mixed (or WaterHeater:Stratified).

That WaterHeater:Mixed is then on the supply side of another plant loop, and on the demand side you place all three chillers in parallel (their condenser nodes). The Pump for that loop can be "virtual" with a very low pressure rise and almost 0 power used.

The three chillers are then on the supply side of the Chilled water loop (evaporator side), serving the building load.

Here's a showcase of my Pinta (Paint) skills:

image description


An alternative may be to use just two loops and to manually set a large Plant Loop Volume for the PlantLoop "condenser water loop".

Julien Marrec's avatar
29.7k
Julien Marrec
answered 2020-02-20 03:59:35 -0500
edit flag offensive 0 remove flag delete link

Comments

mayks's avatar mayks (2020-02-20 06:12:56 -0500) edit

Is the Cooling Tower operation controlled by the temperature of the tank? (with a bypass not shown?)

Julien Marrec's avatar Julien Marrec (2020-02-20 07:38:46 -0500) edit

yes the cooling tower is controlled by the tank I didn´t draw the bypass pipes, but they all have

mayks's avatar mayks (2020-02-20 07:47:55 -0500) edit
add a comment see more comments
1

I see what you have done, but my system is composed by two differnt loops each one with a different coolingTower and chiller but ther are connected through the tank. Can I still do it as you? My system is in the link below

link text

mayks's avatar
61
mayks
answered 2020-02-20 04:09:47 -0500
edit flag offensive 0 remove flag delete link

Comments

This should have been a comment and not an answer. I'm getting a 403 (forbidden access) at the link you gave.

Julien Marrec's avatar Julien Marrec (2020-02-20 05:15:28 -0500) edit

https://drive.google.com/drive/folder...

I think now it will work

mayks's avatar mayks (2020-02-20 05:35:44 -0500) edit