How can I solve: CheckWarmupConvergence: Loads Initialization

The simulation in open studio works but I get the same "severe" message for all my thermal zones. My building is large and contains a lot of thermal mass. During the simulation there was no internal load present and also no HVAC (with HVAC and with internal loads I get the same "severe" message).

Is this bad? And how can this be solved?

image description

thibaut_carrein's avatar
61
thibaut_carrein
asked 2020-01-23 10:23:37 -0500
__AmirRoth__'s avatar
4.4k
__AmirRoth__
updated 2020-01-25 14:17:45 -0500
edit flag offensive 0 remove flag close merge delete

Comments

add a comment see more comments

1 Answer

2

If you're using the OpenStudio application, you can go to the Simulation Settings tab, expand Simulation Control, and increase the "Maximum Number Of Warmup Days" above the default of 25.

image description

If that doesn't help, there are also inputs for "Temperature Convergence Tolerance Value" and "Loads Convergence Tolerance Values" that could be changed as a fallback.

shorowit's avatar
11.8k
shorowit
answered 2020-01-23 10:52:16 -0500, updated 2020-01-23 10:54:49 -0500
edit flag offensive 0 remove flag delete link

Comments

Thank you for the quick response. If I increase the value to 40, the problem is solved.

With how much can you raise it?

thibaut_carrein's avatar thibaut_carrein (2020-01-23 11:25:21 -0500) edit