Performance curves in HVAC templates in Energyplus

Where is the information regarding what type of performance curves are used when we model HVAC using HVAC templates in Energy plus?

Rshree's avatar
123
Rshree
asked 2020-01-18 06:34:12 -0500
__AmirRoth__'s avatar
4.4k
__AmirRoth__
updated 2020-01-18 10:02:50 -0500
edit flag offensive 0 remove flag close merge delete

Comments

add a comment see more comments

1 Answer

2

Going from memory.... The type of curve depends on the E+ object that's in use. You may know that when you run a template, the IDF file gets expanded into a complete, non-template IDF. Find out which objects are created in that new IDF and use curves of interest to you. Next, search the Input Output Reference which is included in the E+ documentation for the object of interest and it will tell you which curve type are acceptable

Jim Dirkes's avatar
3.5k
Jim Dirkes
answered 2020-01-19 04:59:55 -0500
edit flag offensive 0 remove flag delete link

Comments

1

As a note, the "complete, non-template IDF" that Jim refers to ends in [file_name].expidf (short for "expanded IDF") instead of [file_name].idf (file that defines HVAC templates). This expanded IDF is created by the pre-processor tool named ExpandObjects, which can be used stand-alone before running a simulation or after you run a simulation with EP-Luanch by default.