2

How are lighting schedules applied in EnergyPlus?

Hello, what does the following E+ snippet of code mean? "Schedule:Compact, LIGHT-SCHED, Fraction, Through: 12/31, For: Weekdays, Until: 05:00, 0.05, Until: 07:00, 0.1, Until: 08:00, 0.3, Until: 17:00, 0.9, Until: 18:00, 0.7, Until: 20:00, 0.5, Until: 22:00, 0.3, Until: 23:00, 0.1, Until: 24:00, 0.05,"

For example: "Until: 17:00, 0.9" does it mean that from 8:00 to 17:00 the lights are on for 90% of the time OR that the office uses 90% of the maximum wattage of lights during the whole time?

Thank you.

Alex Vlachokostas's avatar
928
Alex Vlachokostas
asked 2015-03-31 10:46:15 -0500
__AmirRoth__'s avatar
4.4k
__AmirRoth__
updated 2015-07-10 09:07:06 -0500
edit flag offensive 0 remove flag close merge delete

Comments

add a comment see more comments

1 Answer

4

If the Lights object uses this schedule, then the load (W, W/ft2, W/person) will be multiplied by these values. From the I/O document:

Field: Schedule Name

The name of the schedule that modifies the lighting power design level (see Design Level Calculation Method field and related subsequent fields). The schedule values can be any positive number. The electrical input for lighting in a particular timestep is the product of the design level and the value of this schedule in that timestep. If the design level is the maximum lighting power input the schedule should contain values between 0.0 and 1.0.

MatthewSteen's avatar
10.1k
MatthewSteen
answered 2015-03-31 11:07:37 -0500, updated 2015-03-31 11:15:57 -0500
edit flag offensive 0 remove flag delete link

Comments