1

Radiant Low Temperature Hydronic

Hello, Could anyone please explain me how the radiant low temperature works? or is there any scheme of the system? (there is an example file in EnergyPlus but I don't understand it) and I cant find any scheme of the underfloor heating.

mayks's avatar
61
mayks
asked 2019-10-22 11:40:06 -0500
Aaron Boranian's avatar
14.1k
Aaron Boranian
updated 2019-11-28 04:19:12 -0500
edit flag offensive 0 remove flag close merge delete

Comments

add a comment see more comments

1 Answer

1

I am assuming you already know how to use EnergyPlus (setting thermal zones, constructions, ZoneHVAC):

  • Create a new Construction:InternalSource. Refer to the linked I/O reference about what inputs are needed and what they are.
  • Assign the construction to your floor surface of the zone(s) with the underfloor heating.
  • Create a new ZoneHVAC:LowTemperatureRadiant object, either VariableFlow or ConstantFlow. Add it to the zone(s) equipment list(s).
  • Make the appropriate connections to your heating PlantLoop.

The ZoneHVAC:LowTemperatureRadiant objects are not controlled by your zone thermostat, instead, they have an separate temperature schedule that will look at the metric that you select in the Temperature Control Type parameter.

Luis Lara's avatar
2.1k
Luis Lara
answered 2019-10-24 10:14:42 -0500, updated 2019-10-24 10:15:39 -0500
edit flag offensive 0 remove flag delete link