VERY high latent load autosizing

I'm modeling an indoor greenhouse. The watering of plants creates very high internal latent load. Concurrent with that, the plant evapotranspiration causes a sensible cooling effect. Overall, it's a very unusual sizing problem - at least I think it is for E+ autosizing.

Regardless, E+ is NOT controlling humidity very well for the chilled water system I've defined :(

Can you provide any tips for proper setup for autosizing in this situation?

Jim Dirkes's avatar
3.5k
Jim Dirkes
asked 2019-10-02 06:38:10 -0500
MatthewSteen's avatar
10.1k
MatthewSteen
updated 2019-10-02 13:20:02 -0500
edit flag offensive 0 remove flag close merge delete

Comments

add a comment see more comments

1 Answer

1

After more experience.... E+ does NOT autosize latent loads well. Manual sizing works well, but requires preparation of a load calculation and equipment sizes :(