Baseline HVAC system [closed]

For the 5 floors office building

EnergyPlus question's avatar
269
EnergyPlus question
asked 2019-08-21 17:41:59 -0500
__AmirRoth__'s avatar
4.4k
__AmirRoth__
updated 2020-01-19 12:10:32 -0500
edit flag offensive 0 remove flag reopen merge delete

Closed for the following reason "the question is answered, right answer was accepted" by EnergyPlus question 2019-09-11 10:02:14 -0500

Comments

add a comment see more comments

1 Answer

4

Table G3.1.1A states that if your source is electric (proposed) you have to chose one option in the last column, therefore system 2, 4, 6 or 8 depending on the number of floors, the building type and the area. In your case I would say the you have to use System 6 for you baseline model since you have 5 floors.

Gio's avatar
1.1k
Gio
answered 2019-08-22 03:48:04 -0500
edit flag offensive 0 remove flag delete link

Comments

2

only exception might be if using 90.1-2016 Appendix G which is based on climate zone (3b = fossil fuel = Systems 3/5/7/9). Question isnt specific. But agree otherwise. All Electric = Systems 4/6/8/10)

dradair's avatar dradair (2019-08-22 11:40:52 -0500) edit
2

90.1-2013 Appendix G is also based on climate zone, so like 90.1-2016, climate zone 3b would be fossil fuel so system would be 5.

anchapin's avatar anchapin (2019-08-26 06:57:32 -0500) edit
2

Yes you are right, my answer was related to the 90.1-2007 that (if I'm not wrong) do not contain any exception based on climate zone.

Gio's avatar Gio (2019-08-26 07:52:11 -0500) edit