getting different results for each run with radiance-based Openstudio simulations without changing the model

I am trying to do both daylighting and thermal simulation using Radiance and EnergyPlus through OpenStudio. My simulation is being completed successfully but whenever i re-run the same model (with no modification) i get a slightly different results for both lighting, cooling and heating loads. is there someone who had the same problem? how did you solve the issue? what can be the cause?

also i have put two daylighting controls in my model, but when i run the simulation i get the message that my secondary daylighting control was ignored. what could be the cause? I have set the primary daylighting control to 0.75 of the thermal zone and the secondary is set to control 0.25 of the thermal zone.

angie123's avatar
21
angie123
asked 2019-07-08 23:24:27 -0500
__AmirRoth__'s avatar
4.4k
__AmirRoth__
updated 2019-07-14 12:38:50 -0500
edit flag offensive 0 remove flag close merge delete

Comments

add a comment see more comments

1 Answer

2

You will always get slightly different results from the Radiance daylighting simulation. This begs the question: how different are they?

The Radiance daylighting measure only works off the primary daylighting control, which is why you are getting that warning about ignoring the second one. That measure was done as a proof of concept and is missing a lot of functionality, but was never funded beyond the initial development.

rpg777's avatar
7k
rpg777
answered 2019-07-09 12:36:43 -0500