How to connect chilled water loop to PAU coil and Chilled Beam coil in series?

I want to connect chilled water loop to PAU coil and Chilled Beam coil in series as below.
image description
However, I cannot find a way how to move chilled beam coil in plant loop as shown below.
Can anyone tell me how to do that?
image description

katsuya.obara's avatar
2.1k
katsuya.obara
asked 2019-07-07 00:58:14 -0500
__AmirRoth__'s avatar
4.4k
__AmirRoth__
updated 2020-01-20 12:03:53 -0500
edit flag offensive 0 remove flag close merge delete

Comments

add a comment see more comments

1 Answer

4

After creating your chilled water coils in each component, you should be able to find the PAU coil under the My Model section of OpenStudio on the right when you are editing HVAC diagrams. Follow these steps to have the two chilled water coils in series:

  • Go to the HVAC Systems tab of OpenStudio and select the chilled water loop (same loop from your screenshot above)
  • Click on My Model near the top right corner
  • Click on Coil Cooling Water (you should see the name of the PAU cooling coil)
  • Drag and drop the PAU cooling coil upstream (to the right) of the chilled beam coil on the demand side of the chilled water loop

When finished, the chilled water loop should look like the screenshot below.

image description