Modeling boiler fan in EnergyPlus

Is a boiler draft fan modeled via the Parasitic Electric Load field? If so, is there a way to define the load via a function? The Engineering Reference appears to imply a fixed determination of hourly boiler parasitic electric power (equal to parasitic electric load specified by the user (W) multiplied by the boiler operating part-load ratio).

pajordan's avatar
576
pajordan
asked 2019-06-26 14:36:28 -0500
MatthewSteen's avatar
10.1k
MatthewSteen
updated 2019-06-27 09:44:15 -0500
edit flag offensive 0 remove flag close merge delete

Comments

add a comment see more comments

1 Answer

1

Yes, a draft fan would be appropriate to model using the "Parasitic Electric Load" field in the Boiler:HotWater object. It is a constant electric input whenever the boiler is operating. If your boiler fan modulates so that it is a variable amount of electricity is used depending on other factors, you may be able to simulate that using the Energy Management System in EnergyPlus. I have not tried that specifically but I believe that it can be done..

JasonGlazer's avatar
6.8k
JasonGlazer
answered 2019-07-03 07:25:46 -0500
edit flag offensive 0 remove flag delete link