LoadProfile:Plant in AirLoopHVAC

Is it possible to use a LoadProfile:Plant object on the demand side of an AirLoopHVAC, to model the air flow requirements, instead of connecting the plant to a thermal zone?

In the InputOutput Reference they only mention the case of coupling it with a water loop, but there is no mention of air loops. Anyone tried it? Thanks

jack_l's avatar
305
jack_l
asked 2019-06-19 09:07:13 -0500, updated 2019-06-19 09:07:54 -0500
edit flag offensive 0 remove flag close merge delete

Comments

add a comment see more comments

1 Answer

2

The plant load profile must be connected to a water loop using the inlet/outlet node fields and is also only called by the (water) plant. For these reasons this object cannot be connected to an air loop.