Unmet hours on official DOE reference building results!
Has anyone else realized that there are high number of unmet hours on the commercial reference building results posted here. https://www.energycodes.gov/developme... This obviously skews the energy results and makes the comparisions of difference standards and codes impossible. Am I looking at the latest thing? Is there a more up to date version that covers IECC 2018 and corrects the unmet hours issue?
Comments
Some examples below.
90.1-2016 Large Office in Buffalo
Time Setpoint Not Met During Occupied Heating 231.75
Time Setpoint Not Met During Occupied Cooling 308.00
90.1-2013 Large Office in Buffalo
Time Setpoint Not Met During Occupied Heating 231.25
Time Setpoint Not Met During Occupied Cooling 332.50
90.1-2010 Large Office in Buffalo
Time Setpoint Not Met During Occupied Heating 258.25
Time Setpoint Not Met During Occupied Cooling 738.00