Why cooling loads appear during the cold months ? Heating/Cooling loads using E+

I am simulating a residential building (80 m2) using Energy-Plus to determine the Heating/Cooling loads through a typical meteorological year. for this purpose, I am using a simple HVAC with Zone control:Thermostat object.So, the aim is to predict the District:Cooling and District:Heating. Indeed, we now that cold months usually require heating loads only. however, as we look at the figure bellow, there are cooling loads in all months of the year. Any help !!!!!

image description

tassimo4.0's avatar
115
tassimo4.0
asked 2019-02-28 13:00:50 -0500
__AmirRoth__'s avatar
4.4k
__AmirRoth__
updated 2019-03-03 11:50:52 -0500
edit flag offensive 0 remove flag close merge delete

Comments

add a comment see more comments

1 Answer

3

The winter building loads are impacted by the under-slab ground temperatures and whether or not the simulation considers infiltration. Without these (offsetting) loads, internal gains can cause the need for cooling in winter.

rraustad's avatar
13.8k
rraustad
answered 2019-02-28 13:10:17 -0500
edit flag offensive 0 remove flag delete link

Comments

Mr Richard Raustad, thanks a lot for your prompt response. In my silumation, I used an infltration of about 0.5 Air-changer/hour. In this case, we can say that the results are reasonable.

tassimo4.0's avatar tassimo4.0 (2019-02-28 13:26:15 -0500) edit

How to solve this problem? I got the same problem, but it doesn't matter construction,,