airflow network air distribution error in E+

Hi! I am getting the following warning message while modelling AirflowNetwork in EnergyPlus:

 ** Severe  ** The number of entered AirflowNetwork:Distribution:Component:Fan objects is 1
   ** Severe  ** The number of entered AirLoopHVAC objects is 0
   **   ~~~   ** Both numbers should be equal. Please check your inputs.
   **  Fatal  ** GetAirflowNetworkInput: Errors found getting inputs. Previous error(s) cause program termination.
   ...Summary of Errors that led to program termination:
   ..... Reference severe error count=2
   ..... Last severe error=The number of entered AirLoopHVAC objects is 0

I am modelling a HVAC loop with only a supply fan on the supply side and an ideal load on the demand side. The fan is modelled as a constant volume fan and connected to the airloop of the HVAC, so i don't understand when the error says that the number of AirLoopHVAC objects is 0.

Could you please help me? Here is the link

Thank you

elenc's avatar
11
elenc
asked 2019-02-21 07:30:39 -0500
shorowit's avatar
11.8k
shorowit
updated 2019-02-21 17:47:13 -0500
edit flag offensive 0 remove flag close merge delete

Comments

add a comment see more comments

1 Answer

1

Your IDF has several Schedule:File objects, so I can't run it, but I do see that your AirflowNetwork:SimulationControl object has the control field set to MultizoneWithoutDistribution, which is probably not what you want. Set that to MultizoneWithDistribution and see if you get a better result or better error message. It's possible that EnergyPlus is getting confused by some other problem and not quite giving you the feedback you need.

Jason DeGraw's avatar
2.2k
Jason DeGraw
answered 2019-03-01 11:29:35 -0500
edit flag offensive 0 remove flag delete link

Comments

Thank you. changing the control field helped.

elenc's avatar elenc (2019-03-06 04:45:36 -0500) edit