1

Energy input ratio as a function of temperature curve output is not equal to 1.0

 ** Warning ** GetElectricEIRChillerInput: Chiller:Electric:EIR="MAIN CHILLER"
 **   ~~~   ** Energy input ratio as a function of temperature curve output is not equal to 1.0 (+ or - 10%) at reference conditions.
 **   ~~~   ** Curve output at reference conditions = 1.256
l1023's avatar
141
l1023
asked 2019-01-28 04:23:01 -0500
shorowit's avatar
11.8k
shorowit
updated 2019-01-28 10:33:19 -0500
edit flag offensive 0 remove flag close merge delete

Comments

add a comment see more comments

1 Answer

2

The curve that you are referencing in "Electric Input to Cooling Output Ratio Function of Temperature Curve Name" should be equal to 1 at the reference conditions set by "Reference Leaving Chilled Water Temperature" and "Reference Entering Condenser Fluid Temperature"

To learn more, please read the InputOutputReference for the Chiller:Electric:EIR object.

JasonGlazer's avatar
6.8k
JasonGlazer
answered 2019-01-28 07:46:45 -0500
edit flag offensive 0 remove flag delete link

Comments

add a comment see more comments