Why my unconditioned zone is having mean RH greater than 90% ?

Hi,

I have made a model to simulate a hospital having both conditioned and unconditioned zones. I have provided a water cooled chiller for AHUs and a cooling tower. The conditioned zones are meeting comfort criteria. The unconditioned zone although temperature is similar to ambient, but the mean humidity for all unconditioned zones are always greater than 90%. I don't think it is practical, because making the loads minimum also is having more than 90% humidity.

Can somebody help?

Regards, Smruti

Smruti's avatar
43
Smruti
asked 2019-01-22 07:23:47 -0500
dhollman's avatar
397
dhollman
updated 2019-03-05 06:58:27 -0500
edit flag offensive 0 remove flag close merge delete

Comments

add a comment see more comments

2 Answers

2

This usually means there is no infiltration to the unconditioned zones. Some form of mass transfer between the unconditioned zones and other conditioned zones (mixing, cross-mixing, ventilation, etc) or outdoors (infiltration or ventilation) should solve the problem.

rraustad's avatar
13.8k
rraustad
answered 2019-01-22 07:52:22 -0500
edit flag offensive 0 remove flag delete link

Comments

add a comment see more comments
0

@rraustad, thank you very much for the reply.

Yes now the unconditioned zones are working fine.

But, I want to mention one observation here.

image description

This outdoor air specification for ventilation doesn't work for unconditioned zones.

When, I changed to infiltration to 5 ACH, it worked, as in image below:

C:\fakepath\2.png

Could someone explain this?

Regards, Smruti

Smruti's avatar
43
Smruti
answered 2019-01-22 23:57:31 -0500
edit flag offensive 0 remove flag delete link

Comments

add a comment see more comments