What to do with Radiation system condensation

 
** Warning ** ZoneHVAC:LowTemperatureRadiant:VariableFlow [B-1 RADIANT CEILING]
   **   ~~~   ** Surface [B1-CEILING] temperature below dew-point temperature--potential for condensation exists
   **   ~~~   ** Flow to the radiant system will be shut-off to avoid condensation
   **   ~~~   ** Predicted radiant system surface temperature = 23.85
   **   ~~~   ** Zone dew-point temperature + safety delta T= 24.50
   **   ~~~   **  Environment=SHANGHAI ANN CLG .4% CONDNS DB=>MWB, at Simulation time=07/21 00:15 - 00:30
   **   ~~~   ** Note that a -1.0000 C safety was chosen in the input for the shut-off criteria
   **   ~~~   ** Note also that this affects all surfaces that are part of this radiant system
l1023's avatar
141
l1023
asked 2019-01-22 00:54:15 -0500
shorowit's avatar
11.8k
shorowit
updated 2019-01-23 09:48:19 -0500
edit flag offensive 0 remove flag close merge delete

Comments

add a comment see more comments

1 Answer

1

Review the following ZoneHVAC:LowTemperatureRadiant:VariableFlow object input fields:

and change them as necessary in your model to reflect the operation you want.

ericringold's avatar
10.6k
ericringold
answered 2019-01-23 09:13:11 -0500, updated 2019-01-23 09:13:32 -0500