VRF performance curve: EIR boundary temperature

I tried a simple case of VRF system with EnergyPlus v9.0. I reported the outputs "Performance Curve Input /Output Value" for the VRF model performance curve called "Cooling Energy Input Ratio Boundary Curve", which gave me a result of -999. However, the rest of the cooling curves have good values. In fact, the selection between the low and high cooling EIR curve seems to be following the boundary temperature curve for cooling capacity, not for EIR.

Can anyone confirm if this is a bug or correct me if I am wrong, please?

Bárbara Torregrosa's avatar
171
Bárbara Torregrosa
asked 2019-01-14 11:12:03 -0500
edit flag offensive 0 remove flag close merge delete

Comments

add a comment see more comments

1 Answer

2

It appears your assessment is correct. The VRF model looks only at the cooling capacity boundary curve to calculate both the capacity and EIR modifiers. The code below shows the issue. This needs to be split out to test each boundary curve individually.

// recalculate cooling Cap and EIR curve output if using boundary curve along with dual Cap and EIR curves.
if (VRF(VRFCond).CoolBoundaryCurvePtr > 0) {
    CoolOABoundary = CurveValue(VRF(VRFCond).CoolBoundaryCurvePtr, InletAirWetBulbC);
    if (OutdoorDryBulb > CoolOABoundary) {
        if (VRF(VRFCond).CoolCapFTHi > 0) TotCoolCapTempModFac = CurveValue(VRF(VRFCond).CoolCapFTHi, InletAirWetBulbC, CondInletTemp);
        if (VRF(VRFCond).CoolEIRFTHi > 0) TotCoolEIRTempModFac = CurveValue(VRF(VRFCond).CoolEIRFTHi, InletAirWetBulbC, CondInletTemp);
    }
}
rraustad's avatar
13.8k
rraustad
answered 2019-01-14 11:19:33 -0500
edit flag offensive 0 remove flag delete link

Comments

Issue #7127 opened on GitHub here