Does anyone know what the two different columns for unheated and heated slabs represent in Table A6.3 ? Why are there different F-Factors for the same horizontal insulation distance and the same R-value? The example below that is highlighted is that if I have a slab with 12 inches of R-5 horizontal insulation is the F-Factor 0.72 or 0.61?

image description

TaylorRoberts's avatar
2.9k
TaylorRoberts
asked 2015-03-12 15:30:43 -0500
__AmirRoth__'s avatar
4.4k
__AmirRoth__
updated 2017-05-08 15:59:02 -0500
edit flag offensive 0 remove flag close merge delete

Comments

Does anyone know the basis of this table?

Joe Huang's avatar Joe Huang (2015-03-13 09:27:18 -0500) edit

These values come from work David Baylon and Mike Kennedy did for the state of Washington. See this publication for more background.

Neal Kruis's avatar Neal Kruis (2015-03-13 15:07:22 -0500) edit

Hhhmmm. That's interesting. These numbers are somewhat lower than those in my 1988 paper. I guess I'll have to read the Baylon paper to find out how he and Mike got the F-Factors. I just did a regression of the fluxes to the Inside-Outside Air Temp Difference, so the F-Factors can vary depending on location.

Joe Huang's avatar Joe Huang (2015-03-13 18:49:39 -0500) edit
1

I fixed the broken link for Neal's comment above.

Anna Osborne Brannon's avatar Anna Osborne Brannon (2017-09-05 20:25:19 -0500) edit
add a comment see more comments

1 Answer

8

It's an error in the table. The second set of values for unheated and heated slabs should be for vertical insulation, not horizontal. See the errata sheet for ASHRAE 90.1-2007 from August 15, 2011. Your 12 inches of R-5 horizontal insulation has an F-Factor of 0.72.