How to simulate the on/off time for an FCU using OS or E+?

Hi all: I am working on an FCU serving an open office. I want to simulate the FCU working status, compare with the actual working status to check if they match. In my model, I have an indoor setting temperature, supply air temperature, etc. seems I can simulate the FCU working time because it should depend on the indoor temperature. but in OS, the FCU has a schedule, "Always On Discrete", I am not sure how it impacts the simulation. I was wondering know if there is any way to simulate the on/off time for the FCU using Open Studio or E+? or can I decide the time using the simulated temperature? Thanks and any comments are welcome!

Westely's avatar
131
Westely
asked 2018-11-12 00:30:33 -0500
__AmirRoth__'s avatar
4.4k
__AmirRoth__
updated 2018-11-12 09:17:08 -0500
edit flag offensive 0 remove flag close merge delete

Comments

add a comment see more comments

1 Answer

1

See the ZoneHVAC:FourPipeFanCoil object documentation in the E+ Input/Output reference.

Availability Schedule:

"The name of the schedule (ref: Schedule) that denotes whether the fan coil unit can run during a given time period. A schedule value greater than 0 (usually 1 is used) indicates that the component can be on during the time period. A value less than or equal to 0 (usually 0 is used) denotes that the component must be off for the time period. If this field is blank, the schedule has values of 1 for all time period"

The fan coil will turn on when:

1) There is a zone request to serve a heating or cooling load, and

2) the fan coil is available to run per the availability schedule.

See the E+ engineering reference for more details on how zone HVAC equipment is controlled.

To determine run time, set the Capcity Control Method input to CyclingFan, and add the HVAC,Average,Fan Coil Runtime Fraction Output Variable.