How to set opening factors correctly?

For modelling cooling effects of natural ventilation in an atrium, I use the airflow network in energyplus to simulate the natural ventilation. To control the conditions and calculate the change of cooling loads, I use the HVAC template Zone: Ideal Load Air system, and fix indoor temperature in 21 degree.

To control the natural ventilation, I use temperature as Ventilation control mode, and in the Ventilation Control Zone temperature setpoint schedule, I use 20.999 degree. Then, in the indoor and outdoor temperature difference lower limit for maximum venting open factor and upper limit, I set 9 and 9.001 to ensure the openings to be opened in 12-21 degree and opening factors in only 0 and 1.

However, I found the opening factors still have some values less than 1.0, like 0.5, why?

there is my filelink text and resultslink text

Thanks

Haohan Sha's avatar
289
Haohan Sha
asked 2018-11-07 08:50:39 -0500
edit flag offensive 0 remove flag close merge delete

Comments

add a comment see more comments

1 Answer

1

This is because I set the Output:variable in the hourly, and energyplus will automatically calculate the average of opening time. I change it to the "detail", it can be found that the open factor only have 1 and 0.

Furthermore, to set open factors based on a complex conditions, for example, relating to the both of outdoor temperature and humidity, I recommend using the EMS in the energyplus.