Temperature control type of LowTemperatureRadiant

Hi

I'm using EnergyPlus to model a TABS system using ZoneHVAC:LowTemperatureRadiant:ConstantFlow. For Temperature Control Type I'm using the OutdoorDryBulbTemperature. Is it possible to use 2 control parameters for my TABS system? E.g.: I want my TABS to be active in winter when the OutdoorDryBulbTemperature is below 8°C AND if the Operative Temperature is not above 18°C. Thanks in advance!

kenny.c's avatar
177
kenny.c
asked 2018-11-07 05:35:14 -0500
__AmirRoth__'s avatar
4.4k
__AmirRoth__
updated 2018-11-07 07:32:20 -0500
edit flag offensive 0 remove flag close merge delete

Comments

add a comment see more comments

1 Answer

2

You'll need to write an EnergyPlus Energy Management System program to accomplish this control scheme.