AirLoopHVAC has no Controllers.

Hi....I´m running a model of an office building. I don´t have errors in the simulation, but I need to know if the error "GetAirPathData: AirLoopHVAC="AIR LOOP HVAC 1" has no Controllers" has to be fixed or can be dismissed. Thanks

vnchavez's avatar
41
vnchavez
asked 2018-10-30 16:07:30 -0500
__AmirRoth__'s avatar
4.4k
__AmirRoth__
updated 2018-10-31 08:14:17 -0500
edit flag offensive 0 remove flag close merge delete

Comments

add a comment see more comments

1 Answer

3

If there are no water coils in the air loop or outdoor air system (i.e., contained within the AirloopHVAC object) then this warning can be ignored. Not sure why this warning is still reported when there are no water coils.