Specifiying cooling coil and baseboard heater capacity

The Coil:Cooling:Water does not seem have a way specify the capacity as Coil:Heating:Water does. For LEED we need to specify the exact capacity as per design how do we do this.

Also for the Baseboard the outputs from do not seem to provide a capacity other than a U Factor times area value. How can we know the actual design capacity of the coils.

kbk78's avatar
601
kbk78
asked 2018-10-12 10:05:11 -0500
__AmirRoth__'s avatar
4.4k
__AmirRoth__
updated 2018-10-12 10:23:01 -0500
edit flag offensive 0 remove flag close merge delete

Comments

add a comment see more comments

1 Answer

2

You are correct, there is no direct input for capacity when using Coil:Cooling:Water. The results are reported to the eio file for html table.

For the coil, the load used to size the coil is shown as well as the Nominal Total Capacity at the rating point.

Component Sizing Information, Coil:Cooling:Water, MAIN COOLING COIL 1, Design Size Design Coil Load [W], 42031.01138
Component Sizing Information, Coil:Cooling:Water, MAIN COOLING COIL 1, Design Size Design Water Flow Rate [m3/s], 1.50123E-003
Component Sizing Information, Coil:Cooling:Water, MAIN COOLING COIL 1, Design Size Design Air Flow Rate [m3/s], 1.60489
Component Sizing Information, Coil:Cooling:Water, MAIN COOLING COIL 1, Design Size Design Inlet Air Temperature [C], 26.08272
Component Sizing Information, Coil:Cooling:Water, MAIN COOLING COIL 1, Design Size Design Inlet Water Temperature [C], 7.22000
Component Sizing Information, Coil:Cooling:Water, MAIN COOLING COIL 1, Design Size Design Outlet Air Temperature [C], 12.80000
Component Sizing Information, Coil:Cooling:Water, MAIN COOLING COIL 1, Design Size Design Inlet Air Humidity Ratio, 1.11374E-002
Component Sizing Information, Coil:Cooling:Water, MAIN COOLING COIL 1, Design Size Design Outlet Air Humidity Ratio, 8.47862E-003
! <Water Cooling Coil Capacity Information>,Component Type,Name,Nominal Total Capacity {W},Nominal Sensible Capacity {W},Nominal Latent Capacity {W},Nominal Sensible Heat Ratio, Nominal Coil UA Value {W/C}, Nominal Coil Surface Area {m2}
Water Cooling Coil Capacity Information,Coil:Cooling:Water,MAIN COOLING COIL 1,43294.78,29077.08,14217.70,0.67,5089.86,51.62

For the ZoneHVAC:Baseboard:RadiantConvective:Water, you are right again. Even though there is an input for Heating Design Capacity, the result is not reported. This would certainly make it difficult to know what the baseboard capacity is. I think this is a mistake and should be corrected.

 ZoneHVAC:Baseboard:RadiantConvective:Water,
  HeatingDesignCapacity,   !- Heating Design Capacity Method
  autosize,                !- Heating Design Capacity {W}
rraustad's avatar
13.8k
rraustad
answered 2018-10-12 13:31:08 -0500
edit flag offensive 0 remove flag delete link

Comments

So the only way to ensure the cooling coil capacity matches with a predetermined system size is to make sure that the loads on the coil result in the same autosize capacity?

kbk78's avatar kbk78 (2018-10-15 08:54:12 -0500) edit

I think that's where you stand at this point while I check into why the Coil:Cooling:Water does not have a Nominal Capacity input and why the baseboard doesn't report autosized heating capacity.

rraustad's avatar rraustad (2018-10-15 16:10:22 -0500) edit

Are there any plans to address this in the near future.

kbk78's avatar kbk78 (2019-10-07 11:52:25 -0500) edit

Not that I know of. You can always request changes via the E+ Git issue page. You need to describe the problem, using examples makes it easy to understand, like including the eio results for baseboard sizing results from the eio file or html tables.

rraustad's avatar rraustad (2019-10-07 13:31:48 -0500) edit

was this baseboard sizing ever fixed?

TheEnergyTutor's avatar TheEnergyTutor (2022-05-09 09:51:51 -0500) edit