Cooling load even when the room temperature are well below the cooling Setpoint

I am getting cooling rate in the month of January even when the room temperature is below the cooling set point.

manavmahan's avatar
21
manavmahan
asked 2018-10-09 10:10:51 -0500
__AmirRoth__'s avatar
4.4k
__AmirRoth__
updated 2018-10-15 19:11:35 -0500
edit flag offensive 0 remove flag close merge delete

Comments

Software? EnergyPlus? OpenStudio? DesignBuilder?

__AmirRoth__'s avatar __AmirRoth__ (2018-10-09 12:38:55 -0500) edit

Please see, I am also getting chiller electric energy in the month of January when the zone temperature is less than 20 and cooling Setpoint is 25 C.

manavmahan's avatar manavmahan (2018-10-11 09:26:35 -0500) edit
add a comment see more comments

1 Answer

2

VAV systems are typically controlled on a supply air set point temperature. If the supply air temperature set point is below the air temperature entering the VAV system, then the cooling coil will operate. Once you run a simulation you can review the rdd file (you must have Output:VariableDictionary,IDF; in your input file to create the rdd file) and choose report variables to view after the simulation completes. Look at the air temperatures (System Node Temperature) and control node set point temperatures (System Node Setpoint Temperature) to see if the controls are the issue. You could simply look at the cooling coil to see what's happening. In your input file a SetpointManager will be used to place a set point at the coil control node, which is typically the coil outlet node. Look at these reports to inspect the operation of the VAV system.

Output:Variable, Cooling Coil Inlet Node Name, System Node Temperature, hourly;
Output:Variable, Cooling Coil Outlet Node Name, System Node Temperature, hourly;
Output:Variable, Cooling Coil Control Node Name, System Node Setpoint Temperature, hourly;
rraustad's avatar
13.8k
rraustad
answered 2018-10-10 11:59:32 -0500, updated 2018-10-11 09:36:58 -0500
edit flag offensive 0 remove flag delete link