Difference of cooling capacity between cooling coil total cooling rate + fan and VRF heat pump total cooling rate

I am trying to do a simple simulation to understand the link between all the output in Energy plus. I have used a HVAC templates system / zone VRF. No ventilation. No sizing factor. One thermal zone.
When I check the output, I have a difference of cooling capacity (in W) between : cooling coil total cooling rate + fan electric power is different than VRF heat pump total cooling rate.
I have : 16802.43 + 119.89 is not equal to 17763.99.
I have tried many simulations by changing some parameters but I always have a difference. Its not a lot but I would like to understand before extending my model.
What did I forget ? Or what is the reason of this difference ?
Thank for your help

Alexis's avatar
545
Alexis
asked 2018-10-01 22:06:51 -0500, updated 2018-10-02 19:46:57 -0500
edit flag offensive 0 remove flag close merge delete

Comments

add a comment see more comments

1 Answer

2

Without seeing your input file the other influence I can think of at the moment is piping losses (see report variable: VRF Heat Pump Indoor Unit Piping Correction for Cooling). However 5% does seem large so if this doesn't resolve the difference then update the numbers and I'll check again.

rraustad's avatar
13.8k
rraustad
answered 2018-10-03 08:14:35 -0500
edit flag offensive 0 remove flag delete link

Comments

I dont have this report variable. I checked and double checked in my rdd file. Nothing about piping loss.
But it seems to be that because when I set the lenght and the height at 1 m, my cooling coil total cooling rate + fan electric power + piping loss is almost equal to VRF heat pump total cooling rate.
I am using E+ v8.7, perhaps this output is arrived after this version ?

Alexis's avatar Alexis (2018-10-03 20:22:01 -0500) edit
1

The piping correction report is only for AirConditioner:VariableRefrigerantFlow:FluidTemperatureControl. At least you now know why there is a difference in the reports. Good job on figuring that out.

rraustad's avatar rraustad (2018-10-04 07:51:10 -0500) edit