Energyplus : Calculation of cooling coil design UA failed for coil CHW CLG COIL

Can anyone please tell me why this error might appear ?

Calculation of cooling coil design UA failed for coil CHW CLG COIL Bad starting values for UA * ~~~ * Coil design UA set to 49770.080623 [W/C]

Siv's avatar
653
Siv
asked 2018-09-28 02:13:32 -0500
__AmirRoth__'s avatar
4.4k
__AmirRoth__
updated 2018-09-28 08:30:39 -0500
edit flag offensive 0 remove flag close merge delete

Comments

add a comment see more comments

1 Answer

4

This is likely caused by a discrepancy in the Coil:Cooling:Water object design temperature/humidity ratio, plant water temperature (Sizing:Plant), Sizing:System supply air temperature (assuming an air loop coil) or Sizing:Zone supply air temperature (assuming a zone coil) inputs. Feel free to ask more questions on this subject.