How is outdoor air applied in OpenStudio?

Hi all! I've got a few questions on how OA is applied in Open Studio.

If I build a system like an AHU with an airloop I know you can add an outdoor air system within the air loop. But if using a PTAC or DX Split System, is OA introduced by mixing with the RA stream before the coil?

Also, if I'm modeling a large apartment complex and each unit will have a dedicated small OA fan (20-30 CFM) do you think it would be acceptable to model this by creating one airloop with a supply fan, connecting it to the outside and applying a terminal diffuser to each zone?

JCR562's avatar
121
JCR562
asked 2018-09-22 10:43:24 -0500
__AmirRoth__'s avatar
4.4k
__AmirRoth__
updated 2018-09-22 13:57:43 -0500
edit flag offensive 0 remove flag close merge delete

Comments

add a comment see more comments

1 Answer

2

For ZoneHVAC equipment such as PTAC (packaged terminal air conditioner), fan coil, etc., outdoor air is mixed with return air in the unit. DX split systems are typically modeled as an airloop system.

For the large apartment complex application, yes, a single airloop to provide OA to multiple zones should be identical to multiple single-zone OA units.

MJWitte's avatar
9.7k
MJWitte
answered 2018-10-11 15:31:16 -0500
edit flag offensive 0 remove flag delete link

Comments

Thanks MJWhite, much appreciated.