Water mass flow evaporative cooler

Is there any way to define or control the water mass flow for a direct evaporative cooler in EnergyPlus?

I am using the "EvaporativeCooler:Direct:ResearchSpecial" object but you can't define or control the water mass flow that the evaporative coolers use.

Charalampos Angelopoulos's avatar
386
Charalampos Angelopoulos
asked 2018-09-15 10:49:48 -0500
edit flag offensive 0 remove flag close merge delete

Comments

add a comment see more comments

1 Answer

3

No, there is not a way to model a specified water flow rate. The models assume fully wetted media and consume only the amount of water that evaporates into the air stream. The rest of the water flow is assumed to recirculate.

MJWitte's avatar
9.7k
MJWitte
answered 2018-09-25 13:56:54 -0500
edit flag offensive 0 remove flag delete link

Comments

Thank you for your help!