what is the exact values to be inputted in Cooling Coil DX Single Speed?

I am doing an EnergyPlus simulation using the actual air-conditioning units of the building. The ACU's are window type therefore, I used the ZoneHVAC:WindowAirConditioner of the IDF and that also needs the data of the cooling coil to used. Now, I used the Cooling Coil DX Single Speed and I find it difficult on what values be inputted in the following: 1. Gross Rated Cooling Capacity 2. Gross Rated Heat Sensible Ratio 3. Rated Air Flow Rate

I would like to ask a help on how to solve this values or are there any constants to multiplied since I modeled an actual 2.5 horsepower ACU.

Philip Caesar Ebit's avatar
181
Philip Caesar Ebit
asked 2018-08-27 21:56:08 -0500
__AmirRoth__'s avatar
4.4k
__AmirRoth__
updated 2018-08-28 09:50:29 -0500
edit flag offensive 0 remove flag close merge delete

Comments

add a comment see more comments

1 Answer

3

Look up the data on the manufacturers site. Your AC unit has a model number, google that number and look up the specifications. Manufacturers data will include the data your looking for, total rated capacity, SHR (or they show total and sensible capacity where SHR = sensible/total), and air flow rate. Look for the data at 35 C (95 F) outdoor dry-bulb temperature and 19.44 C (67 F) indoor wet-bulb temperature and use that data to input your HVAC unit.

rraustad's avatar
13.8k
rraustad
answered 2018-08-31 20:03:15 -0500
edit flag offensive 0 remove flag delete link

Comments

okay Sir Richard, thank you for these information.