Is it possible to change the convective/radiant fraction of the idealloadsairsystem?

I want to easily model an air system a water radiator heating system and an underfloor heating/cooling system. I am looking for a way to change the convective/radiant fraction of the Ideal Air Loads System. I do not want to model an HVAC system so I would just want to give an indication to energy plus of how much of the energy is due to convection or due to radiation without modelling anything more complicated (object, connections etc).

Mana's avatar
21
Mana
asked 2018-08-24 09:40:23 -0500
__AmirRoth__'s avatar
4.4k
__AmirRoth__
updated 2018-08-25 11:02:40 -0500
edit flag offensive 0 remove flag close merge delete

Comments

add a comment see more comments

2 Answers

3

No, ZoneHVAC:IdealLoadsAirSystem is 100% convective. There is no way to change that.

MJWitte's avatar
9.7k
MJWitte
answered 2018-08-28 17:15:13 -0500
edit flag offensive 0 remove flag delete link

Comments

add a comment see more comments
1

As has been mentioned before, this is not possible, but you can achieve the same result by using a ZoneHVAC:Baseboard:RadiantConvective:Electric object. See also further post.