Heating equipment sizing and people load

Hello All, Is the internal heat gain from occupants taken into account for heating equipment sizing? Thanks

S's avatar
111
S
asked 2018-07-31 13:39:06 -0500
__AmirRoth__'s avatar
4.4k
__AmirRoth__
updated 2018-08-06 07:55:04 -0500
edit flag offensive 0 remove flag close merge delete

Comments

add a comment see more comments

1 Answer

1

Hi, normally not accounting heat gain from people for heating sizing (so building equipment can met peak heating demand also when it is unoccupied). But if yuo want to take in consideration a base gain of people in some circustances (i.e. any constant occupation for cerain particular building type) you can revise the schedule:compact of the people occupancy and improve your specific schedule (period and fraction) for the WinterDesignDay (that normally is set to zero). Furthermore, check plant and/or equipment oversizing factor for an accurate evaluation between sizing and peak heat demand.