Hello,

I am trying to model DOAS which has seasonal OA mass flow. To model this, I am trying to use SetpointManager:Scheduled - Control Type MassFlowRate with which flow can be controlled in different seasons. However, I see constant airflow after applying the SetpointManager with desired Mass flow Rate as described in I/O file.

Any pointer will be appreciated in this regard.

Thanks,

Javed's avatar
273
Javed
asked 2018-07-23 14:25:39 -0500
__AmirRoth__'s avatar
4.4k
__AmirRoth__
updated 2018-07-23 15:32:03 -0500
edit flag offensive 0 remove flag close merge delete

Comments

add a comment see more comments

1 Answer

1

Virtually nothing in EnergyPlus responds to a mass flow rate setpoint.

Use AirTerminal:SingleDuct:ConstantVolume:NoReheat with a DesignSpecification:OutdoorAir object. You can use the "Outdoor Air Schedule Name" to modify the terminal unit flow request seasonally.