How can i fix supply air temperature for VRF in EnergyPlus?

Hi! Now I am modelling a building equipped with VRF system. Even though generally supply air temperature of Japanese VRF is higher by 10 degrees Celcius than zone setpoint temperature, the model now i am modelling supplies in approximately 41 degrees Celcius. so i want to fix the VRF supply air temperature as 32 degrees celcius. how can i do this?

i've already tried SetpointManager:FollowSystemNodeTemperature. but it didn't work. additionally, SetpointManager:Warmest and SetpointManager:WarmestTemperatureFlow don't work for VRF systems

joooon's avatar
119
joooon
asked 2018-07-03 02:31:49 -0500, updated 2018-07-03 02:36:51 -0500
edit flag offensive 0 remove flag close merge delete

Comments

add a comment see more comments

1 Answer

2

Set the Zone Heating Design Supply Air Temperature field in your Sizing:Zone objects to 32°C.

mdahlhausen's avatar
9.5k
mdahlhausen
answered 2018-07-03 17:55:56 -0500
edit flag offensive 0 remove flag delete link

Comments

thank you for your answer! i will try this! :)

joooon's avatar joooon (2018-07-04 05:32:32 -0500) edit