how to find weighted exceedance (We), hours of exceedance (He), operative temperature in the building , using energy plus .please help me out with how to proceed?

i want to find weighted exceedance(We), hours of exceedance(He), operative temperature in the building , using energy plus .please help me out with how to proceed? how to get these variables in results ?

vasss's avatar
21
vasss
asked 2018-07-02 05:53:28 -0500
__AmirRoth__'s avatar
4.4k
__AmirRoth__
updated 2018-07-05 07:52:26 -0500
edit flag offensive 0 remove flag close merge delete

Comments

add a comment see more comments

1 Answer

1

If you will ask for output of the following variables: Zone Air Temperature, Zone Thermostat Heating Setpoint Temperature and and Zone Thermostat Cooling Setpoint Temperature at hourly rate you will be able to calculate what ever you need.

For the hour of exceedance you can use those four output variables:

Zone Heating Setpoint Not Met Time

Zone Heating Setpoint Not Met While Occupied

Zone Cooling Setpoint Not Met Time

Zone Cooling Setpoint Not Met While Occupied Time

You can read about output variables in the Input Output Reference .

You can look at that result for the search I made in Google for weighted exceedance (We).

One more thing is that in OS at the OpenStudio Result Measure you will find few lines of the top the unmethours tolerance which I think by default is set to 0.37 deg R.

Avi's avatar
4.3k
Avi
answered 2018-07-04 14:41:43 -0500, updated 2018-07-05 02:54:11 -0500
edit flag offensive 0 remove flag delete link

Comments

thank you so much for answering . but after i find out the variables u mentioned in your answer , how to use them to find He and We?

vasss's avatar vasss (2018-07-05 01:42:37 -0500) edit