EMS Outdoor Air Node for Cooling Towers

Hello Everyone,

I would like to modify the outdoor air inlet node of a Cooling Tower. The issue is I can't find the variable, there is only an outdoor air inlet node for the AHU in the OutdoorAir:NodeList. The help file states that "If this field is left blank, the outdoor air conditions entering the cooling tower are taken directly from the weather data". But I only want to modify the outdoor air node entering the coolign tower but I don't seem to find this variable.... Could any want provide me with any suggestions? Any help would be greatly appreaciated, thank you!

Fustrated

Fustrated's avatar
111
Fustrated
asked 2018-06-24 01:50:06 -0500
__AmirRoth__'s avatar
4.4k
__AmirRoth__
updated 2018-06-25 16:32:14 -0500
edit flag offensive 0 remove flag close merge delete

Comments

add a comment see more comments

1 Answer

1

Just create a new node name and use it in the cooling tower Outdoor Air Inlet Node Name and add it to the OutdoorAir:NodeList.