Design load with sizing factor is lower than Calculated design load [closed]

My Design Load With Sizing Factor is 33.14 tons which is lower than my Calculated Design Load of 48.69 tons. I didn't input a sizing factor for my zones so it should be using a default value of 1.15, correct? Why is this lower than the calculated design load? The air flows have a similar trend.

image description

Saroop's avatar
85
Saroop
asked 2018-06-19 00:59:47 -0500
__AmirRoth__'s avatar
4.4k
__AmirRoth__
updated 2018-06-19 10:39:22 -0500
edit flag offensive 0 remove flag reopen merge delete

Closed for the following reason "the question is answered, right answer was accepted" by Saroop 2018-06-19 11:06:58 -0500

Comments

add a comment see more comments

1 Answer

2

No, if blank or zero, the Zone Cooling (heating) Sizing Factor will be replaced by the global Sizing:Parameters.

By default the Sizing:Parameters sizing factors are 1.25 for heating and 1.15 for cooling (corresponding to ASHRAE Appendix G), but you may have changed them. These can be viewed/set on the "Simulation Settings" tab:

image description

Julien Marrec's avatar
29.7k
Julien Marrec
answered 2018-06-19 02:45:00 -0500
edit flag offensive 0 remove flag delete link

Comments

Thanks for the response. I didn't change the sizing factors in simulation settings, so they are using those values. 1.25 for heating and 1.15 for cooling. I now realized that I input a Cooling Design Air Flow Rate and that value is being for the sizing factor calculations.

Saroop's avatar Saroop (2018-06-19 11:06:13 -0500) edit

Ok glad you figured it out!

Julien Marrec's avatar Julien Marrec (2018-06-19 13:46:02 -0500) edit