Inlet Node Name is required but was blank

Dear all, I 've been trying a single zone for HVAC analysis for a while, simulation always ends badly. The most and big problem shows" field [ xxx Inlet/outlet Node Name] is required but was blank, and I check a lot of discussion in the forum which is similar to this one. But unfortunately, even I delete extra setting coils still can't fix it out.

Could someone please kindly help me on this issue? I'll be appreciated!

Attached file here.

Borui

borui's avatar
73
borui
asked 2018-06-12 07:04:56 -0500
__AmirRoth__'s avatar
4.4k
__AmirRoth__
updated 2018-06-12 08:39:47 -0500
edit flag offensive 0 remove flag close merge delete

Comments

add a comment see more comments

1 Answer

3

You have two problems: one is really easy to fix, the other is much more tricky (for new users at least).

Problem 1: trivial

** Severe  ** <root>[Coil:Heating:Water][Coil Heating Water 1] - Missing required property 'water_inlet_node_name'.
** Severe  ** <root>[Coil:Heating:Water][Coil Heating Water 1] - Missing required property 'water_outlet_node_name'.

The message should point you directly to the fix. If you look at your coil Heating water, it is placed only on your AirLoopHVAC, and it doesn't have a connection to a PlantLoop. I just connected it properly to the PlantLoop.

HW Coil Not connected

Problem 2: harder

You have one heating coil on your plantLoop, but this coil isn't on an AirLoopHVAC. Similarly, "CHW Clg Coil 2" and "Fan Constant Volume 4" are nowhere to be found... This is because you actually have an orphaned "AirLoopHVACUnitarySystem" in your model (orphaned=not placed on an AirLoopHVAC) and this unitary system contains the Fan, the heating coil, and the cooling coil. I removed it via the ruby bindings:

unitary = m.getAirLoopHVACUnitarySystems[0]
unitary.remove

Now your model will run correctly. I have uploaded the fixed model here. Please note that it was upgraded to OpenStudio 2.5.1 (the version I have on my system), so you won't be able to load it in OpenStudio 2.4.0.

Julien Marrec's avatar
29.7k
Julien Marrec
answered 2018-06-12 08:32:46 -0500
edit flag offensive 0 remove flag delete link

Comments

Hi Julien, really thanks for your help. But I still have some more questions.

The orphaned issue might because I tried various HVAC system before and I wanna see what's the difference but it doesn't work, so after that, I delete them. I just assumed that it's clear but true is not... So, how to detect the invisible error in HVAC system? Measures?

And the other question is when pre-assigned in the Thermal zone equipment as a PTAC, but to the next page HVAC system doesn't show up any details, like hot water loop or the PTAC system itself, how to prevent that or make it right?

Really thanks!

borui's avatar borui (2018-06-14 23:12:35 -0500) edit

I found your oprhaned object via the ruby bindings, but you could find it in a text editor, but removing it in a text editor wouldn't be safe: chances are you'll forget or mess up something in the process. On the thermal Zone tab, when you click on your PTAC you should see a link icon in the right panel, that's allow you to connect the hot water coil to a plant loop.

Julien Marrec's avatar Julien Marrec (2018-06-15 05:10:32 -0500) edit

(FYI, I'm answering here because you're new, but 1. This is a new question that has nothing to do with this one, so it shouldn't be posted here, and 2. You could find the answer on this site by yourself, it's been covered more than once.)

Julien Marrec's avatar Julien Marrec (2018-06-15 05:10:48 -0500) edit

Big thanks to Julien, I got it! Next time I'll be careful about that.

borui's avatar borui (2018-06-16 13:12:03 -0500) edit