Why shading system reduces heating energy demand if it's only available during summer?

I implemented windows shading systems in my building energy model. The simulation results show a reduction of the cooling energy consumption but also a reduction of the heating energy consumption. I don't understand why this happens since the shading system is available only during the cooling season.

Does anyone know why this happens?

Cristina's avatar
95
Cristina
asked 2018-05-26 03:34:51 -0500, updated 2018-05-27 11:53:59 -0500
edit flag offensive 0 remove flag close merge delete

Comments

Please add a tag that specifies what software you are using, e.g., 'openstudio', 'designbuilder', 'equest', etc. Thx.

__AmirRoth__'s avatar __AmirRoth__ (2018-05-26 12:31:11 -0500) edit

@Cristina could you post a link to your model?

Avi's avatar Avi (2018-05-29 02:51:30 -0500) edit
add a comment see more comments

1 Answer

3

Make sure that the unshaded window construction matches the base model. Take the input file with shading and set the shade controls to be off at all times. This should produce results identical to the unshaded model. If not, review the shading control inputs.