Equation of a system energy provided to the zone in EnergyPlus engineering reference

In Eq (2.3) at Engineering reference v.8.5.0 is as follows. Qsys=msys x Cp x (Tsup – Tz) (2.3)

where Qsys is system energy provided to the zone, msys is system air flow rate, Cp is zone air specific heat, Tsup is supply air enthalpy, Tz is enthalpy of the air leaving the zone. There are no units in document.

So, I guess, Qsys is W, msys is kg/s or CMH, Cp is kJ/kgK, Tsup and Tz are kJ/kg. In this case, overall units do not match.

Am I wrong or typo?

tobeabest's avatar
11
tobeabest
asked 2018-04-24 23:53:21 -0500
edit flag offensive 0 remove flag close merge delete

Comments

add a comment see more comments

1 Answer

1

Tsup and Tz are temperature in C. I think you are confusing these 2 equations:

Q = Mdot * Cp * (Tsup - Tz)

and

Q = Mdot * (Hsup - Hz)
rraustad's avatar
13.8k
rraustad
answered 2018-04-25 09:18:13 -0500
Julien Marrec's avatar
29.7k
Julien Marrec
updated 2018-04-25 10:25:34 -0500