Outside Air -Ideal Loads
I need the hourly outdoor-air flow for my buildings. Normally I export my hourly data to an excel sheet with a measure. For the outside air, I tried to use Output:Variable,*,Zone Ideal Loads Outdoor Air Mass Flow Rate,hourly; !- HVAC Average [kg/s]
, but the excel file is full of zeros. The same with Zone Ideal Loads Outdoor Air Sensible Heating Rate
.
My ratios of outdoor air is defined in the space types in OS:DesignSpecification:OutdoorAir
, with the Sum method and they are not zeros (of course) neither is the schedule.
Does anyone know how I can have access to this data ?
Comments
Do you have a thermostat defined for your zones? (optionally: can you upload your model somewhere and add a link in your question?)
Yes I have thermostat in my model. The other Output Variables like Zone Ideal Loads Zone Total Heating Energy, are okay.
So, I think you're requesting the right variable
Zone Ideal Loads Outdoor Air Mass Flow Rate
, so there must be something else at play here, your model would help troubleshooting.Check the resulting IDF file, to ensure the ZoneHVAC:IdealLoadsAirSystem does have its
Design Specification Outdoor Air Object Name
set correctly too.