Water Heater:Heat Pump - Tank Doing Majority of Heating

I'm modeling a Water Heater:Heat Pump in Openstudio and am having trouble with the attached tank doing ALL of the water heating. I've tried a couple of things like adjusting the capacity and volume of the tank down to 1, but that just seems to remove that load completely. I've also tried to increase the capacity of the DX Coil in the HPWH, but that had no effect. Any ideas??

Lindsey Gaunt's avatar
161
Lindsey Gaunt
asked 2018-04-12 17:43:58 -0500, updated 2018-04-12 19:20:00 -0500
edit flag offensive 0 remove flag close merge delete

Comments

add a comment see more comments

1 Answer

4

Solved my own problem!

Had to raise the compressor setpoint temperature higher than the tank setpoint.