Monodraught windcatcher IES

I'm having difficulty simulating a naturally ventilated space using the Monodraught windcatcher components. The model will run if I don't add any heat gains to the space, however if I add any heat gains the analysis fails due to:

"Instability in room. Possible remedies: reduce time step; set radiant fraction to 0; check gain and ventilation levels; reduce MacroFlo opening areas."

Does anyone have any ideas?

josh.sykes's avatar
181
josh.sykes
asked 2018-04-05 09:57:32 -0500
__AmirRoth__'s avatar
4.4k
__AmirRoth__
updated 2018-04-05 10:45:39 -0500
edit flag offensive 0 remove flag close merge delete

Comments

add a comment see more comments

1 Answer

2

Monodraught helped me get to the bottom of this. Should anyone have a similar problem in the future see below:

The thermal template assigned to the windcatchers and associated ducts should be "Monodraught WINDCATCHER/Duct" for some reason this was not being pulled in when adding the windcatcher components. Having manually loaded the template and applied it to the relevant spaces the model runs fine.

josh.sykes's avatar
181
josh.sykes
answered 2018-04-06 08:31:59 -0500