Measure entrance temperature of supply air into the room and exit temperature in the control volume

I am quite a noob in E+, I need those temperatures as it required by my cost function. Also, I have some concern about estimating currrent air mass in a room. Thanks in advance

Sultan Yerumbayev's avatar
93
Sultan Yerumbayev
asked 2018-03-14 15:48:08 -0500
Julien Marrec's avatar
29.7k
Julien Marrec
updated 2018-03-29 06:34:41 -0500
edit flag offensive 0 remove flag close merge delete

Comments

add a comment see more comments

1 Answer

2

You can add this measure from BCL, select 'include demand side nodes' in the options and using DView, check the temperatures of the nodes in the airloop just before and after the thermal zones. You can also refer this unmethours post