Setup for primary air loop supplying to multiple AHU's in OpenStudio

OpenStudio

I want to set up an outdoor air pretreat air loop with heating/cooling coils and a constant speed fan supplying preconditioned air to other AHU's. How do I setup such primary and secondary air loop? I am wondering about how to connect the AHU's on the demand side. image description Can this be set up in OpenStudio and how?

rkbest's avatar
1.4k
rkbest
asked 2018-03-13 12:58:22 -0500, updated 2018-03-13 14:32:10 -0500
edit flag offensive 0 remove flag close merge delete

Comments

add a comment see more comments

1 Answer

2

EnergyPlus currently doesn't support an air loop serving multiple other air loops. There was work in that direction, but it appears to have stalled out.

See here for discussion of workarounds for that design.