Adjacent floors can't have different constructions

I try to model a building in which 2 rooms have different floors, due to some servers that are installed there in these rooms. Basically these two rooms have a floor that consists of three layers (thin metal layer, marmoleum and floor tiles), while the other rooms only consists of a concrete layer. The following error occurred in OpenStudio:

* Severe * GetSurfaceData: Construction INTERIOR FLOOR INSTALLATION of interzone surface SURFACE 89 does not have the same materials in the reverse order as the construction INTERIOR FLOOR CONCRETE of adjacent surface SURFACE 116

The surfaces are seperated by a wall (the floors are in different rooms). Could someone help me with this?

Mans_sopers's avatar
187
Mans_sopers
asked 2018-02-28 07:50:07 -0500
edit flag offensive 0 remove flag close merge delete

Comments

add a comment see more comments

1 Answer

3

If surface 89 and surface 116 represent floor surfaces of adjacent spaces then they should not reference each other as outside boundary objects. What is the origin of the geometry and surface matching of the model?

If these two surfaces represented the shared wall or shared floor/ceiling surface between the spaces then the constructions used for each surface need to be mirrors of each other.

David Goldwasser's avatar
20.4k
David Goldwasser
answered 2018-02-28 08:29:53 -0500
edit flag offensive 0 remove flag delete link

Comments

I checked it again and apparently one the ceiling of the basement was not divided into different surfaces. I fixed it and it works now, thanks.

Mans_sopers's avatar Mans_sopers (2018-02-28 12:56:54 -0500) edit

Glad you figured it out! In a case like that even if you had the constructions correct there would have been EnergyPlus warnings about breaking conservation of energy laws because matched surfaces are not the same size (don't know if it looks for exact same or has a tolerance before it warns you)

David Goldwasser's avatar David Goldwasser (2018-02-28 13:12:10 -0500) edit

I didn't had any warnings earlier on, so maybe the surfaces were split up but the thermal zone was the same. To fix the problem I only split the two basement parts into two different thermal zones. Thanks for the explanation anyways!

Mans_sopers's avatar Mans_sopers (2018-02-28 13:17:07 -0500) edit