The Zone Window Transmitted Solar Radiation Rate doesn't change when window is open while modeling an operable window. It remains the same as a closed window with a given SHGC Value. What changes should I make in my model ?

I am modeling a naturally ventilated building. I need to know the exact solar radiation entering the zone when the window is open. However, I discovered that the solar radiation entering the room doesn't change when the window is open. What changes should I make in my model to get this to work ?

Thank you

niharkopal's avatar
121
niharkopal
asked 2018-02-22 05:30:28 -0500
__AmirRoth__'s avatar
4.4k
__AmirRoth__
updated 2018-02-22 07:18:07 -0500
edit flag offensive 0 remove flag close merge delete

Comments

add a comment see more comments

1 Answer

4

Yes, EnergyPlus Airflow Network (Natural Ventilation) does not affect the thermal properties of operated windows. An approach would be using EMS Surface Construction State actuator to change the window properties (to a clear glass), which involves certain experience with EMS to sync those changes with the opening of the windows.

ecoeficiente's avatar
638
ecoeficiente
answered 2018-02-22 15:56:17 -0500