Economizer limit in eQUEST

Hello,

I am working on eQuest 3.64 and the project has an economizer that allows up to ~60% design airflow to be OSA.

Is there an input for eQuest that allows this maximum to be present without impacts DCV controls?

Thanks,

Michael

mjadamss's avatar
53
mjadamss
asked 2018-02-14 14:40:38 -0500
__AmirRoth__'s avatar
4.4k
__AmirRoth__
updated 2018-02-15 08:38:29 -0500
edit flag offensive 0 remove flag close merge delete

Comments

add a comment see more comments

1 Answer

2

Yes. Use the keyword "Max-OA-Fraction" to set a limit on the fraction of OSA when economizer operates. This keyword input is available in eQuest as one of the economizer input boxes in the graphical user interface.

Molly Curtz's avatar
1.3k
Molly Curtz
answered 2018-02-14 16:05:49 -0500, updated 2018-02-14 16:25:25 -0500
edit flag offensive 0 remove flag delete link

Comments

Thanks Molly! i have no idea how I neglected to see that input box!