Why is there no heat rejection energy from air cooled VRF?

Is it always included in the (air cooled) compressor energy?

There is cooling energy, but I would expect to see some condenser fan energy under heat rejection. I did not see any way to connect condenser fans, so I assume that the assumption was the condenser fan energy is always rolled up with the compressor.

Openstudio 2.3.0

CRHavis's avatar
103
CRHavis
asked 2018-01-16 17:59:03 -0500
bbrannon4's avatar
1.7k
bbrannon4
updated 2018-01-17 22:10:18 -0500
edit flag offensive 0 remove flag close merge delete

Comments

add a comment see more comments

1 Answer

5

In EnergyPlus, compressor energy for air-cooled AirConditioner:VariableRefrigerantFlow objects are included under Cooling:Electricity, not HeatRejection:Electricity. You can look at the .mtd output file to see which equipment is included on which meters.