the difference between "Cooling Coil Sensible Cooling Rate"and"Zone Predicted Sensible Load to Cooling Setpoint Heat Transfer Rate"

The module i used is HVAC Template:Zone:FanCoil .

I found there is a little difference between "Cooling Coil Sensible Cooling Rate" and "Zone Predicted Sensible Load to Cooling Setpoint Heat Transfer Rate".

What is the difference between these two?

image description

Richard's avatar
85
Richard
asked 2018-01-04 21:38:17 -0500
__AmirRoth__'s avatar
4.4k
__AmirRoth__
updated 2018-01-05 08:24:39 -0500
edit flag offensive 0 remove flag close merge delete

Comments

add a comment see more comments

1 Answer

2

The zone predicted sensible load tells you how much energy is needed to meet the thermostat set point temperature. The cooling coil sensible cooling rate tells you how much energy the coil transferred to the air, which also include fan heat and outdoor air load, if any. See if the fan heat accounts for the difference.

rraustad's avatar
13.8k
rraustad
answered 2018-01-05 07:43:57 -0500
edit flag offensive 0 remove flag delete link

Comments

So ,the zone predicted sensible load doesn't include outdoor air sensible load right? The fan heat load is quite little normally, i guess the main difference comes from outdoor air sensible load.

Richard's avatar Richard (2018-01-07 20:21:24 -0500) edit

Yes, zone loads do not include outside air, but coil loads do.